Electric Clint
Member
- Location
- Portland, OR USA
I have a customer that wants us to install an under cabinet lighting module(Ikea) that includes LED lights a standard 120v outlet that are all daisy chained together off the power module. The power module appears to be intended for hard wire and includes a 14/2 W/G flexible cord (SJT 14AWGX3C 105C VW-1 300V). They want it wired to a 20amp circuit with 12/2 romex and a 20 amp breaker. 400.5 Flexible cord ampacity in the 2014 NEC seems to indicate the best I can squeeze out of this cord is 18 amps. But then is it considered fixture wiring attached to a branch circuit? My eyes are glazed over from the NEC. Anyone have any thoughts on this?