jtester
Senior Member
- Location
- Las Cruces N.M.
Previously I posted a question concerning disconnects at sewage aeration ponds. I have found some additional information and am stumped by the State?s decision. Briefly, there are mixers and aerators floating out in this couple acre lined earthen pond. They are held in place by wire rope anchored to the shore. The manufacturer has specified that flexible cord be used to connect the motors with permanent wiring on the shore. The Electrical Bureau has determined that flexible cord or cable can?t be used as a permanent wiring method out to these floating pontoons unless it is part of the UL listing of the assembly. They cite 400.8(1) as the reason. Unfortunately, the whole assembly is not UL listed. I have suggested that 400.7(A)(7) and (9) be considered in this case. The inspectors have rejected those arguments.
Their solution is to wire the motors as temporary wiring, using cord caps and receptacles at shore as the connections. This solution seems to open up a real can of worms as it would introduce Article 590, but I am not successful with the inspectors.
Does anyone have any information relating to listings, or other thoughts relating to 400.7 and 400.8?
Thanks
Jim T
Their solution is to wire the motors as temporary wiring, using cord caps and receptacles at shore as the connections. This solution seems to open up a real can of worms as it would introduce Article 590, but I am not successful with the inspectors.
Does anyone have any information relating to listings, or other thoughts relating to 400.7 and 400.8?
Thanks
Jim T