Flexible Cord lengths/support
Tolman
Albuquerque NM
Master Electrician/Electrical Inspector
I have run into an instance where the contractor has run about 20-30 ft of flexible cord to a permanently mounted LED luminaire. They used TY-Wraps to support the flexible cord and the cord enters a 4x4 J-Box via a listed connector and terminates to the branch CKT hardwired. I believe this is a code violation as 410.62(C)(1) states
shall be permitted to be cord connected provided the luminaire is located directly below the outlet or busway. Would this apply to a hardwire situation? Is hardwiring the cord allowed? Also i am unable to find strapping requirements if in fact running 20FT if flexible cord is allowed.
Understood. Being that the NEC allows fixtures to be wired with flexible cord, is there a distance limitation if they are not using a manufacturer supplied cable?
410.62 details the requirements for cord connected LEDs.
Other than some exceptions, they are to be cord & plug with the fixture located below the receptacle.
That is more or less the conclusion i have come too as well. I cant find any reference that states a flexible cord feeding a permanent luminaire can be hardwired to a branch CKT.
Also no reference on how far above the light the outlet can be or strapping requirements for the flexible cord.
I believe the only time a cord can be hardwired is a FACTORY cord & canopy (covered in 410.62) as shown below............and I know of no length .restriction
Side note: We questioned this type of installation at a halve a billion dollar research center where they used the cord that came with hanging luminares that every 4 or 5th one was on the 277 volt emergency power from the three 2,000 KW gen sets.Cord was thin so guessing no larger then 16/3 feed by 20 amp breakers.
You might find this earlier thread of interest: