jtinge
Senior Member
- Location
- Hampton, VA
- Occupation
- Sr. Elec. Engr
Because on a machine, the NEC doesn't apply; it's (maybe) a UL508A issue. Those glands are intended to be used to get multiple cables / hoses out of industrial control enclosures and into wire tray / onto the machine's frame.In industrial locations, it is not uncommon to see prefabricated flexible cables routed through enclosure walls using a Roxtec cable pass through or something similar. In light of NEC 400.12 (2), how is this code compliant?
View attachment 2560981
View attachment 2560982
The application at our site, that is the basis for my inquiry, is for transitioning cables from a utility corridor to the inside of a clean room between two pieces of equipment. I have used Roxtec in the past to route instrumentation cables into a wind tunnel test section, but admittedly never thought about how the 400.12 (2) requirement may or may not apply. It would be nice to see an exception that explicitly permitted the use of assemblies for specifically designed for routing flexible cables in bulkheads or walls in supervised installations.Because on a machine, the NEC doesn't apply; it's (maybe) a UL508A issue. Those glands are intended to be used to get multiple cables / hoses out of industrial control enclosures and into wire tray / onto the machine's frame.
I can also see them being used to isolate cables as they pass into "clean room" areas, for instance; they're very good at that. "Engineering supervision" solves a lot.
Roxtec -type gland plates are used extensively in marine environments, along with flexible cables. Sealing from (salt)water ingress and fire spread are extremely important on ships. Conduit isn't used, as water can pass through the interior of the conduit and cause damage.
SceneryDriver
I believe that might be covered under "engineering supervision." Practically, there are sometimes design situations that need some common sense. I think a clean room application would be one of those. I always read that section as prohibiting some hillbilly from dragging SO cable through the studs of his shack and powering his toaster.The application at our site, that is the basis for my inquiry, is for transitioning cables from a utility corridor to the inside of a clean room between two pieces of equipment. I have used Roxtec in the past to route instrumentation cables into a wind tunnel test section, but admittedly never thought about how the 400.12 (2) requirement may or may not apply. It would be nice to see an exception that explicitly permitted the use of assemblies for specifically designed for routing flexible cables in bulkheads or walls in supervised installations.
Guess I'm wondering if "where run through holes in walls, structural ceilings...." was intended to apply to cable transit systems or only to a drilled hole?
I would consider a clean room to be under "engineering supervision".So if the picture shown in the OP was on a clean room wall...