Flexible cords for forced air units. Article 422.16 Flexible Cords

Madera Wil

Member
Location
200 West Forth St Madera CA 93637
Occupation
Deputy Building Official
I'm read in Article 422.16 Flexible Cords about all the different types of appliances that are permitted to be connected with flexible cords. It does not mention a forced air units.
Someone told me that they are required to be connected with a disconnect and the unit hard wired.
Is this correct? Is there a reference in the code for this?

Thanks for your help.
Mad Wil
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
My memory plays tricks but if I recall correctly UL does not list any AHUs for cord & plug connections.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
My memory plays tricks but if I recall correctly UL does not list any AHUs for cord & plug connections.
I didn't think that any equipment of this type was listed for a cord and plug connection which is why it comes with a KO for the cable or raceway entry and not a cord and plug. In some parts of the country they're wired with flexible cords every day which is a violation,
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Or make one with an inlet and a 3-way switch, which could replace (or be) the disconnect switch.
 
Top