Flexible Cords, High-bay lighting, and amperages

Status
Not open for further replies.

DougM

Member
Location
Danvers, MA, USA
Gentlemen - I have searched this forum already and saw nothing, so I thought I'd post the question.

1) In a retrofit situation, say I'm replacing a 400W Metal Halide high-bay with a new 4-lamp T5 high-bay, or even an LED equivalent. Can the new fixture be supplied with an 18 AWG SO cord? Say the branch circuit is 20A, 277V. There is a junction box nearby that the existing fixture is wired to, either with a plug/receptacle or is hard-wired.

I'm having a kind of back-and forth with a colleague and would like some other input.

Thank you in advance.
 
I would say yes on the cord (based on 400.7) and no on the 18awg (table 400.5). Maybe you could use the 18awg cord with an in-line fuse holder (based on 240.10) but I'll defer to a more experienced member. :D
 
NEC specifically allows listed luminaires to have such small cords, as part of a listed assembly. Think "fixture whip." You can even go up to a 50-amp breaker on the circuit on such an assembly.

While I suspect the code panel was thinking of things like the 'Reloc" system (MC whips), if the fixture came with a cord, I'd say there's enough wiggle room to make this idea allowed.
 