Flexible Cords in Electrical Equipment Room

Status
Not open for further replies.

Crawfish

Member
Hello,

In a commercial building (highschool) equipment room we have a at$T smartjack that requires 110v and it mounted on a wood back board. We need to plug it into our ups on the other side of the room about 25ft away. Rather than pay for an electrician to tap into an existing 110 and intall a new outlet, is it to code to run a flexible cord from the smart jack which has a 3 prong plug over our wiring rack and into our ups. We may also need to install a few clips on the backerboard to secure the wire a bit before it goes across on the wire rack.

Thank you for your time
Aaron
 

pete m.

Senior Member
Location
Ohio
What you are describing sounds to me like a permanent wiring application. If that is the case then rubber cord is not an option. 400.8(1)and(4)