flexible metal conduit

Status
Not open for further replies.

dkstein

Member
need an interpretation on the uses of FMC (a.k.a. greenfield)

I have a situation in a club house on a multi-family apartment complex where I have service disconnects remote from the panels. Due to the 2x6 framing it is not possible to run a rigid type conduit from the disconnects to the panels, because the 90's do not have room to turn in the wall to the building exterior. Going up the outside of the wall in conduit and entering into the attic is out also due to framing issues.

The city will allow the use of romex in the building, so I could use SER for the service feeders, however I need 3/0, and all the local suppliers do not stock such.

The question is, can I use FMC between the disconnects and the panels. The distance is about 30 feet. My first inclination is to say NO, but I would like some input on article 348.
 

tonyi

Senior Member
Re: flexible metal conduit

No problem, flex is fine for long distances, just pull a suitably sized EG for the feeder.

The 6' and 20A stuff in 250 only comes into play if you intended to use the armor as an EG.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: flexible metal conduit

I would only remind you that you may not conceal angle connectors in the wall.

348.42 Couplings and Connectors.
Angle connectors shall not be used for concealed raceway installations.
 