Re: Flexible Metalic Tubing
Welcome Tom, Could this be what you are thinking about?
250.118
(5) Listed flexible metal conduit meeting all the following conditions:
a. The conduit is terminated in fittings listed for grounding.
b. The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).
d. Where used to connect equipment where flexibility is necessary after installation, an equipment grounding conductor shall be installed.