I was recently asked to ground a piece of cord and plug connected equipment by running a ground wire from the faceplate screw on a stainless steel duplex recepticle cover to the metal case on the equipment. According to 250.138 an equipment grounding connection can be made using a flexible wire when connected to an equipment grounding conductor. However, I do not believe that a face plate screw meets the requirements for an equipment grounding conductor (250.118). Secondly, I beleive there is a requirement for a #10 screw treaded into a metal box for bonding (dont recall the code number).
The equipment has a three wire molded cord that includes the grounding conductor plugged into 120vac 20amp recepticle, that is wired properly and passes a circuit test. The owner claims that the equipment is failing a current leak test and needs to pass such test for safety. the equipment is a sign in kiosk with a touch screen display in a lobby waiting area.
Anyone have any advice on this subject? Thanks.
The equipment has a three wire molded cord that includes the grounding conductor plugged into 120vac 20amp recepticle, that is wired properly and passes a circuit test. The owner claims that the equipment is failing a current leak test and needs to pass such test for safety. the equipment is a sign in kiosk with a touch screen display in a lobby waiting area.