Hello, an 8.4kW induction cooktop ran fine on a 40A circuit in an old house. After reconfiguration using a 30A circuit, the controls flicker under load.
Based on Table 220.55 Note 4 (2008) derating the sole cooktop is not permitted (and I'll upgrade the circuit), but the factory leads are 10awg like the branch circuit.
Is the unstable voltage more likely caused by the insufficient wire gauge, or is there something wrong with the wire inside the wall? Thank you.