An engineering firm, that did contract work for us, gave details for installing bonding jumpers by wrapping them several times around the seal-tite raceway, about 3-4 for times per foot. I do not think it the proper way to install them for two reasons:
? Voltage maybe induced into the EGC by coiling it around power conductors
? The coiled EGC may act like a choke circuit, adding impedance to clearing a ground fault
The NEC handbook diagram shows the bonding jumper installed straight along the raceway and fastened with tie-wraps. Most of these installations are in Class 1 Division 2 areas.
Some are contractors are installing them as shown in the handbook, but most are following the drawing details. Does anyone have any comments?