True.Electric
Member
- Location
- South Carolina
- Occupation
- Electrical Contractor
In my area, we have a lot of lakes with floating docks, and it's common practice to wire these docks with basic power for lighting, receptacles, and similar uses. We always bond the system according to NEC Article 555, running the bond back to the panel where power originates, and we also drive an 8-foot ground rod on shore next to the dock. The issue we’re encountering during the summer is stray voltage appearing on the dock—typically anywhere from 0 to 9 volts—carried through the equipment ground and bonding conductors. Anything above 2 volts can be felt when swimming and touching metal components of the dock, which raises serious safety concerns. I’m not an electrical engineer, but my best guess is that this voltage increases with the load on the power grid, often correlating with hotter weather. The best solution we’ve found so far is using a Victron isolation transformer, originally designed for marine applications. We install it at the house to feed the line going through the yard to the shore power panel and then out to the dock. We wire the transformer in a "floating" configuration, bonding ground and neutral (as if it were a boat floating in the water). The other option is and leaving them unbonded, intended for when the boat is trailered. I'm reaching out to see how others feel about this approach. I came up with it myself but haven’t found much documentation or examples online. While I've had dozens of people ask me to do the same for their docks, I don’t want to proceed further until I'm absolutely confident in the safety. Has anyone else run into this issue? Does anyone have a better solution, or a preferred isolation transformer they trust for this application?