I have been seeing a great many sub-panel installations that I think are incorrect. I see the Neutral and EGC connected together in these sub-panels.
I would like some confirmation:
1. If a 50 amp 240V sub-panel, say 5 feet from main panel, connected with EMT, the neutral is to "float" while the EGC bar is connected to the panel. A seprate ECG is not needed since it is connected by the EMT.
2. If a 50 amp sub-panel, say 5 feet from main panel, connected with Romex, 4 wire, the neutral is to "float" while the EGC is connected to the panel.
I look forward to all replies.
I would like some confirmation:
1. If a 50 amp 240V sub-panel, say 5 feet from main panel, connected with EMT, the neutral is to "float" while the EGC bar is connected to the panel. A seprate ECG is not needed since it is connected by the EMT.
2. If a 50 amp sub-panel, say 5 feet from main panel, connected with Romex, 4 wire, the neutral is to "float" while the EGC is connected to the panel.