RTFM... :rant:
^--- intended to be a tad humorous, but it does have serious connotations
Is this an NRTL (UL) listed control cabinet?
Ignoring the NEC "instructions clause" [110.3(b)] for the moment, a required GFCI-protected supply circuit could hinge on what article this pond falls under.
So is it a fountain or a pond?
Having a fountain seems to place it squarely under ARTICLE 680— SWIMMING POOLS, FOUNTAINS, AND SIMILAR INSTALLATIONS, which does not appear to require the supply to be GFCI protected.
If the pond was just a pond without a fountain, that would put it under ARTICLE 682— NATURAL AND ARTIFICIALLY MADE BODIES OF WATER. If not required to have an equipotential plane "All circuits rated not more than 60 amperes at 120 through 250 volts, single phase, shall have GFCI protection." [682.33(A) & (B)]