I have a humidity sensor that I am connecting to a 24VDC Class II power supply. I leave the Class II power supply floating because of instrumentation connected to the power supply. For example, there are sensors that have 4-20mA outputs, as well as 0-5V outputs powered from the power supply.
I also leave the power supply floating to prevent the unintentional grounding of ground referenced test equipment.
When I check for continuity between the ground ring on the Humidity sensor board, and the - com terminal on humidity board, I get no continuity. But, when I power up the sensor, i have approximately 22Volts between the humidity boards -com terminal and the ground washer. My guess is that this means they are coupled together internally by a diode.
The -Com terminal on the humidity sensor is also connected to the - terminal of the 24VDC 60W Class II power supply. This means that my entire Class II 24V circuit is now ground referenced.
Why would the Humidity sensor want to force the circuit to be ground referenced? It has a 0-5V output. The wiring from the sensor to the PID controller it is connected to is about 10+ feet routed through the machinery. Having the signal referenced to ground at two seperate places on the machinery cannot be good for the 0-5V signal...
My question is, why would they have it internally connected to ground like this? The humidity sensor can run off of 24VAC or 24VDC...would the ground ring be for an earth ground if the power supply is a 24VAC transformer? To me, the ground lug on 24VDC Class II power supply powered humidity sensor serves no purpose...:thumbsdown:
I also leave the power supply floating to prevent the unintentional grounding of ground referenced test equipment.
When I check for continuity between the ground ring on the Humidity sensor board, and the - com terminal on humidity board, I get no continuity. But, when I power up the sensor, i have approximately 22Volts between the humidity boards -com terminal and the ground washer. My guess is that this means they are coupled together internally by a diode.
The -Com terminal on the humidity sensor is also connected to the - terminal of the 24VDC 60W Class II power supply. This means that my entire Class II 24V circuit is now ground referenced.
Why would the Humidity sensor want to force the circuit to be ground referenced? It has a 0-5V output. The wiring from the sensor to the PID controller it is connected to is about 10+ feet routed through the machinery. Having the signal referenced to ground at two seperate places on the machinery cannot be good for the 0-5V signal...
My question is, why would they have it internally connected to ground like this? The humidity sensor can run off of 24VAC or 24VDC...would the ground ring be for an earth ground if the power supply is a 24VAC transformer? To me, the ground lug on 24VDC Class II power supply powered humidity sensor serves no purpose...:thumbsdown: