Industrial application is a floating platform (in pond) with 3 - 480 VAC TEFC motors in a Class I, Division 2 area. Motor controller will be on shore.
Looks like Art 682 requires "all" electrical connections to be 30 inches above water level and 12 inches above deck level. I presume this includes the motor connections since the motors are not submersible.
Can SOOW cord be used submerged from shore to the floating platform? If not, what would be a better choice?
Thanks.