Good Morning,
I have a customer with a small business that received an unwelcome guest last Sunday, about 5' of water due to tropical storm Chantal here in Chapel Hill, NC.
The sheetrockers are removing the bottom 6' of sheetrock so that it can be replaced and the inner walls can be dried out.
I was wondering if anyone on this forum could give me some guidelines as to what electrical components should be replaced and what can just be allowed to dry?
The building is in a strip mall that was built in the 70s. However this little business was rewired in 2013 due to another flooding event.
If there is EMT or MC cable involved does that need to be replaced or can it be dried out? If drying is an option can I just point fans at the MC cable to speed up the drying? If it is EMT, can I use a vacuum cleaner to pull the water out of any horizontal sections?
If the EMT has THWN in it I should be able to verify that in the panel. But if the MC cable has THWN or something with a W in the name on it should I be able to see that in the panel?
I left a message with the electrical inspector late Friday for his advice but would like to go beyond what is just necessary.
Thanks for the great advice.
I have a customer with a small business that received an unwelcome guest last Sunday, about 5' of water due to tropical storm Chantal here in Chapel Hill, NC.
The sheetrockers are removing the bottom 6' of sheetrock so that it can be replaced and the inner walls can be dried out.
I was wondering if anyone on this forum could give me some guidelines as to what electrical components should be replaced and what can just be allowed to dry?
The building is in a strip mall that was built in the 70s. However this little business was rewired in 2013 due to another flooding event.
If there is EMT or MC cable involved does that need to be replaced or can it be dried out? If drying is an option can I just point fans at the MC cable to speed up the drying? If it is EMT, can I use a vacuum cleaner to pull the water out of any horizontal sections?
If the EMT has THWN in it I should be able to verify that in the panel. But if the MC cable has THWN or something with a W in the name on it should I be able to see that in the panel?
I left a message with the electrical inspector late Friday for his advice but would like to go beyond what is just necessary.
Thanks for the great advice.