was at a job this week that had 120v receptacles installed in garage slab .inspection was passed was unable to find anything in the code related to this installation . what are you're thoughts . I was shocked . thank you
If a commercial garage with hazardous locations there could be issues, but otherwise there is no general prohibition of floor boxes in a garage. It does need to be suitable for the conditions that will be encountered, which could include a box rated for wet locations.