flouresant fix with 16awg whip

Status
Not open for further replies.

Tori

Senior Member
Location
Maryland
Have any of you seen this ? , At a data center the other day I saw in the ceiling these fixtures hanging on aircraft cable and a little white wire feeding it - upon further inquiries I found out it was 16 awg .:confused:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
240.5(B)(2) Fixture Wire Fixture wire shall be permitted to be tapped to the branch circuit conductor of a branch circuit in accordance with the following:
(1) 20-ampere circuits — 18 AWG, up to 15 m (50 ft) of run length
(2) 20-ampere circuits — 16 AWG, up to 30 m (100 ft) of run length
(3) 20-ampere circuits — 14 AWG and larger
(4) 30-ampere circuits — 14 AWG and larger
 