flourescent lights hung from jack chain . can you use mc or the new type ac solid
Might be an AHJ call
Code leads one to say stranded:
410.56 Protection of Conductors and Insulation.
(E) Stranding. Stranded conductors shall be used for wiring on luminaire chains and on other movable or flexible parts.
I don't see anything in 410.56 refering to 'branch circuit' conductors. Part VI Wiring 'of'
Luminaires, that contains 410.56, does not mention the 'branch circuit' conductors unless
it is specific to them, such as 410.64 and .65 as an example.
410.117(B) , Circuit Conductors, Branch circuit conductors that have an insulation suitible
for the temperature encountered 'shall be permitted' to terminate in the luminare.
IMO. 410.56 is for wiring with-in the fixture, and 410.117 is for wiring to the fixture.