I went to troubleshoot a lighting problem and need some advice. About 5 can lights are dimming every once in awhile for a length of time of about 15 min. I went to the panel and found the breaker. The voltage was ok and the current seemed normal. I checked the phase conductors feeding the panel. The voltage seemed fine on all the phases, but the current on phase B was all over the place ranging from 38 to 58 to 0. The fluctuation of current was rapid. This panel is a three phase 120\208. What do you think this problem is? I am going to hook up a power phase analyzer next.