Flukes Wiggy Replacement

Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
This new meter from Fluke will sell for about $90 I am told.
* Both have three ways to detect ac/dc voltage: light, sound, and vibration
* Both offer the added functionality of a GFCI trip and continuity beeper, plus the convenience of a built-in flashlight
* The T+PRO Electrical Tester comes with a rotary field indicator for troubleshooting three-phase systems, resistance measurement to 9.99 KOhms, as well as a backlit LCD display for easier viewing

In my opinion the wiggy is unsafe as its low impedance and can cause an arc flash. This meter is cat III rated
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
tomorrow I'll post some pictures of an arc fault caused by a wiggy.
I've got to get a fluke t+pro- build in LED flash light, shows voltage by light, sound, vibration, and has a rotary field indication for 3 phase....
 

realolman

Senior Member
I was involved in a pretty lively discussion on this forum when a new electrician wanted advice on what brand DMM to get.

I hadn't used a wiggy in many moons, and never missed it, but after the discussion I ordered one at work . My boss ( no electrician ) asked what that was going to do for us, and I told him that sometimes the DMM will indicate voltage that is "not really there". If the wiggy indicated voltage it "was there".

Now what should I tell my boss?:smile:


I have used the wiggy a few times since, and I can see the point of their advocates, but I just don't care for them, and I think I'd rather see ghost voltage, than not see something that is there.

Just yesterday a new guy and me were working on a circuit and the DMM showed some small voltage. He seemed puzzled and I told him I'd go get the wiggy because it would tell for sure if there was anything worth knowing about there. About halfway back I turned around because I knew it wasn't going to show anything, so what's the point?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The Fluke article on solenoid testers is another good example of somewhat misleading information.
In fact, you must allow for cool-downs (on the order of half a minute) as you take readings with solenoid-based testers.

Of course this is a fact, but the fact that they leave out is that their electronic "wiggy" has a 1 to 10 duty cycle when used at 240 or above.
For voltages above 240 V, you must only connect to a voltage source for a MAXIMUM of 30s and then disconnect for a MINIMUM of 300s.
This is not that much different than a solenoid votlage tester. The following is from the instructions from an Ideal tester.
The duty cycle on:eek:ff ratio is 1:7 for 240 volts or less, and 1:40 for 240 volts or greater. Fifteen seconds is the maximum “On” time.
Also Ideal has a CAT III 600 volt rated solenoid voltage tester.
Don

 