fluorescent fixtures attached to unistrut in rows

Status
Not open for further replies.

dave134

Member
Location
chicago
it was suggested to me to use "jack" chain to support 80' - 100' long rows of fixtures.
I've always been taught to use threaded rod.
is there any NEC code that describes supporting fixtures of this weight?
my guess is jack chain is not listed for this use
 

jusme123

Senior Member
Location
NY
Occupation
JW
it was suggested to me to use "jack" chain to support 80' - 100' long rows of fixtures.
I've always been taught to use threaded rod.
is there any NEC code that describes supporting fixtures of this weight?
my guess is jack chain is not listed for this use

...what weight, you did not list any? I've used jack chain to support fixtures, NEC legal.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
There is not much in the NEC about supporting fixtures, 410 is pretty short. Local building codes are likely a better source.

As far as hanging 100' of flouesents with jack chain- I have no problem with it as long as you use more than one piece on each end.
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
it was suggested to me to use "jack" chain to support 80' - 100' long rows of fixtures.
I've always been taught to use threaded rod.
is there any NEC code that describes supporting fixtures of this weight?
my guess is jack chain is not listed for this use

Typically if you use jack chain you do not use strut. You put the first 8' fixture up with two jack chains located 7' apart and from that point on you add a jack chain every 8' so each jack chain only supports the weight of one fixture.

The number 12 jack chain we use has a 25 pound working load limit.

For a nicer look use aircraft cable in place of jack chain.
 