B bwyllie Senior Member Location MA Nov 14, 2003 #1 Has anybody been aware of fluorescent lighting causing AFCI's to trip. I have heard of this happening in dorm rooms.
Has anybody been aware of fluorescent lighting causing AFCI's to trip. I have heard of this happening in dorm rooms.
T ty Senior Member Location 3rd Rock from the Sun Nov 15, 2003 #2 Re: Fluorescent Lighting in the large houses that we do, almost all of the closets get fluorescent lights and we've never had one trip an arc fault breaker.
Re: Fluorescent Lighting in the large houses that we do, almost all of the closets get fluorescent lights and we've never had one trip an arc fault breaker.
tonyi Senior Member Nov 15, 2003 #3 Re: Fluorescent Lighting I've never seen it. Check the usual suspects - like a bootleg gnd somewhere, or a pinched wire under the ballast cover that actually is arcing.
Re: Fluorescent Lighting I've never seen it. Check the usual suspects - like a bootleg gnd somewhere, or a pinched wire under the ballast cover that actually is arcing.
iwire Moderator Staff member Location Massachusetts Nov 15, 2003 #4 Re: Fluorescent Lighting I agree with Tony. On fixtures that use the compact fluorescent lamps I have many times found the wires pinched between the socket itself and the metal of the fixture.
Re: Fluorescent Lighting I agree with Tony. On fixtures that use the compact fluorescent lamps I have many times found the wires pinched between the socket itself and the metal of the fixture.