faresos

Senior Member
Hello everyone:

What is the minimum size of metal stud is required to install a flush electrical panel for commercial building? Currently the metal stud is 3 5/8" with 5/8" Gyp board at both ends. I don't think this will work, any thoughts?

Thanks,
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Are you talking about a residential type loadcenter or a panelboard? Even though you said a commercial building a loadcenter could possibly be used and most loadcenters are 4" deep whereas a panelboard is generally 5.75" deep.

Roger
 

mgookin

Senior Member
Location
Fort Myers, FL
How high is the wall and what gauge studs are used?
Is it stable now with no panel? Non-loadbearing walls are only required to withstand 5 lb lateral force but if it's wobbly now it's going to be worse if you put a panel in it.
New construction or existing wall?
If code allows one trick is to cut some lumber to install on the far side of each stud. That way you get something to bite into without reducing the width of your framing bay. Run them floor to ceiling if you can.
 

faresos

Senior Member
Are you talking about a residential type loadcenter or a panelboard? Even though you said a commercial building a loadcenter could possibly be used and most loadcenters are 4" deep whereas a panelboard is generally 5.75" deep.

Roger

It's a panelboard 20"W x 5.75" D
 

faresos

Senior Member
How high is the wall and what gauge studs are used?
Is it stable now with no panel? Non-loadbearing walls are only required to withstand 5 lb lateral force but if it's wobbly now it's going to be worse if you put a panel in it.
New construction or existing wall?
If code allows one trick is to cut some lumber to install on the far side of each stud. That way you get something to bite into without reducing the width of your framing bay. Run them floor to ceiling if you can.

It's a new construction and we are in design phase and we can make the wall depth as needed. Normally I ask for 6" stud and never had any issue with it but I'm looking for the minimum stud depth that will work.

Thanks,
 

kwired

Electron manager
Location
NE Nebraska
It's a new construction and we are in design phase and we can make the wall depth as needed. Normally I ask for 6" stud and never had any issue with it but I'm looking for the minimum stud depth that will work.

Thanks,
A standard "2x6" is 5-1/2 inches wide. You get an additional 1/2 or 5/8 from the thickness of drywall applied to it and can flush mount anything under 6 or 6-1/8 inches deep.
 