Hello all,
Two quick questions about flux vector drives:
1. Suppose you have a flux vector drive that is incredibly oversized for the motor lets say you have a motor with an FLA of 100A and the drive is rated for 400A (Heavy Duty) 200% for 3 seconds. So in essence the max torque output is not drive limited.
At 0 RPM what is the motor's max torque output limit in the following two situations:
a. NEMA B motor, and b. NEMA D motor. I know that in each case the drive can produce FLT at 0 RPM, however, if you want to produce lets say 400% FLT (assume that this is more than each motors BDT), the breakdown torques naturally happen at different speeds for the two motor designs, does that matter or will the drive max out torque to the motors BDT value what ever that is?
2. The beauty of the flux vector drive is that it can make AC motors operate like DC motors. Benefit of DC motors is that the field current can be kept constant physically by applying a different source to the field than the armature. The armature current can then be manipulated so that you can have FLT at 0 RPM.
How does the flux vector drive physically keep the magnetizing current in the motor constant while only manipulating the torque producing current? Looking at the simplified circuit diagram of an induction machine, it seems that it can only raise the voltage to the stator of the machine. Is it implicitly forcing this because its maintaining the constant V/Hz ratio? Are the two parameters that it can only really change to the motor are Voltage and Hz?
For reference attached is the simplified induction machine circuit showing the components that the drive sees.
Two quick questions about flux vector drives:
1. Suppose you have a flux vector drive that is incredibly oversized for the motor lets say you have a motor with an FLA of 100A and the drive is rated for 400A (Heavy Duty) 200% for 3 seconds. So in essence the max torque output is not drive limited.
At 0 RPM what is the motor's max torque output limit in the following two situations:
a. NEMA B motor, and b. NEMA D motor. I know that in each case the drive can produce FLT at 0 RPM, however, if you want to produce lets say 400% FLT (assume that this is more than each motors BDT), the breakdown torques naturally happen at different speeds for the two motor designs, does that matter or will the drive max out torque to the motors BDT value what ever that is?
2. The beauty of the flux vector drive is that it can make AC motors operate like DC motors. Benefit of DC motors is that the field current can be kept constant physically by applying a different source to the field than the armature. The armature current can then be manipulated so that you can have FLT at 0 RPM.
How does the flux vector drive physically keep the magnetizing current in the motor constant while only manipulating the torque producing current? Looking at the simplified circuit diagram of an induction machine, it seems that it can only raise the voltage to the stator of the machine. Is it implicitly forcing this because its maintaining the constant V/Hz ratio? Are the two parameters that it can only really change to the motor are Voltage and Hz?
For reference attached is the simplified induction machine circuit showing the components that the drive sees.