I was not pleased to find that an electrical project I was in charge of had a 50' run of FMC from the junction box to the wall receptacle where the copier was going to be plugged in but in reading article 348, It only states the following as being limited to 6' in length:
(1) In wet locations
Listed flexible metal conduit (FMC) is no longer permitted for use in wet locations. Also, for this application, the conductors must be suitable for wet locations. Listed FMC 1/2 in. and larger may be installed in unlimited lengths, provided an equipment grounding conductor is installed with the circuit conductors. See 250.118(5) as well as 348.60 for specific requirements related to the use of FMC as an equipment grounding conductor.
(2) In hoistways, other than as permitted in 620.21(A)(1)
(3) In storage battery rooms
(4) In any hazardous (classified) location except as permitted by other articles in this Code
(5) Where exposed to materials having a deteriorating effect on the installed conductors, such as oil or gasoline
(6) Underground or embedded in poured concrete or aggregate
(7) Where subject to physical damage
Can I please get some input, even though the NEC may permit a 50' run, it does not seem to me that this is in keeping with "neat and workman like", I did not figure that the electricians need thousands of dollars worth of nice portable tools to run FMC all over the place.
(1) In wet locations
Listed flexible metal conduit (FMC) is no longer permitted for use in wet locations. Also, for this application, the conductors must be suitable for wet locations. Listed FMC 1/2 in. and larger may be installed in unlimited lengths, provided an equipment grounding conductor is installed with the circuit conductors. See 250.118(5) as well as 348.60 for specific requirements related to the use of FMC as an equipment grounding conductor.
(2) In hoistways, other than as permitted in 620.21(A)(1)
(3) In storage battery rooms
(4) In any hazardous (classified) location except as permitted by other articles in this Code
(5) Where exposed to materials having a deteriorating effect on the installed conductors, such as oil or gasoline
(6) Underground or embedded in poured concrete or aggregate
(7) Where subject to physical damage
Can I please get some input, even though the NEC may permit a 50' run, it does not seem to me that this is in keeping with "neat and workman like", I did not figure that the electricians need thousands of dollars worth of nice portable tools to run FMC all over the place.