Would it be a violation to connect FMC conduit to PVC conduit? If so, what code section would I reference? Thanks
20amp lighting circuit, 3/4" conduit joined by electrical tapeCan you provide more detail ?
With the proper fittings it should be allowable but things like grounding need to be taken into account.
How are they being joined ? What size conduits/circuit, etc ?
Ok, thanks for your input!Your answer would be in different sections No violation if FMC is allowed. See uses allowed in respective articles. The FMC will need connection at one end to a bonding conductor per 250.118