I need some help here, I wired a 10 door walk in cooler and all the equipment I installed was rated for wet locations which in this area is standard practice.
The problem is all the factory wiring inside the cooler for door heaters and lighting is in 1/2" FMC.
The inspector wants to fail this as he considers it a wet location and FMC is not suitable for that use.
Apparently he does not know about 348.12(1)
[ December 11, 2003, 06:49 PM: Message edited by: iwire ]
The problem is all the factory wiring inside the cooler for door heaters and lighting is in 1/2" FMC.
The inspector wants to fail this as he considers it a wet location and FMC is not suitable for that use.
Apparently he does not know about 348.12(1)
My main question is what do you all do inside a walk in cooler or freezer, do you consider it a dry, damp or wet location?348.12 Uses Not Permitted.
FMC shall not be used in the following:
(1)In wet locations unless the conductors are approved for the specific conditions and the installation is such that liquid is not likely to enter raceways or enclosures to which the conduit is connected
[ December 11, 2003, 06:49 PM: Message edited by: iwire ]