FMC

Status
Not open for further replies.
good morning, an electrician rerouted a pipe to allow for an A/C duct. He cut pipe terminated into a Jbox, installed another jbox and used FMC to tie both boxes and continue run.The length of FMC is 1ft. long. Question. Is this permissible?. Yhank You.
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
And it meets the supporting requirements of 348.30. Which usually states must be supported within 1ft of the box. :)
 