Started a 20 kw generator. It is ge, which has 100 amp breaker in it. Install manual gives a chart, for this model #4 cu or #2 al, 300 v, 75 c. Also defers to 310.15 b 16 per 2011 for correction factors and calcs.
Was not paying attention for wire rating, but 4 is 85, 2 90. So if I had to I could downsize breaker according to 240.6, no 85 breaker.
Inspector had started to challenge on trench inspect. Wire pulled already, #4 cu in pipe to generator, 100 a ser to box in basement to meet up with pipe.
my argument is the book specs it, although it may be wrong, follow manufactures instructions. Or is ge covered since they defer to code?
Was not paying attention for wire rating, but 4 is 85, 2 90. So if I had to I could downsize breaker according to 240.6, no 85 breaker.
Inspector had started to challenge on trench inspect. Wire pulled already, #4 cu in pipe to generator, 100 a ser to box in basement to meet up with pipe.
my argument is the book specs it, although it may be wrong, follow manufactures instructions. Or is ge covered since they defer to code?