Have any of you actually measured neutral current that is higher than the phase current on an otherwise reasonably balanced 208/120Y system?
The reason I ask is I researched this quite a bit several years ago when K-rated transformers and 200% neutral busses were relatively new and being pushed heavily by the gear reps.
I used to work at a MAC school university with 18,000 students, 40 buildings and dozens (100's?) of computer labs. Most of the buildings were older and the labs were converted classrooms or other spaces. No new K-rated transformers were installed nor were any 200% neutrals. Power for the labs was just added to whatever was available.
I took numerous measurements with a Fluke 41 or 41B (can't remember now) harmonic analyzer. Not once did I ever find true RMS neutral current near any one of the phases or close to exceeding the conductor ampacity (pretty much all "full size" neutrals). I would routinely see high current distortion but voltage distortion was almost always under 3%. If it was higher than that it was not by much.
I do agree that, on paper, triplen harmonics will add but the distortion from PC's and other power supplies occurs at random angles and ends up having a cancelling effect anyway. In order to reach the 173% theoretical maximum neutral current you'd have to have condition just perfect for that with your loads and that just will never happen.
Again, anyone actually seen a transformer failure that you were absolutely certain was due to harmonic current and/or higher neutral current than phase current?
I never have and I've measured a bunch of locations. I'm wondering how much of this "problem" is scare tactic and how much is real. I know the trade magazine sure make a big deal out of it and have for years.
thanks,
bbaumer
The reason I ask is I researched this quite a bit several years ago when K-rated transformers and 200% neutral busses were relatively new and being pushed heavily by the gear reps.
I used to work at a MAC school university with 18,000 students, 40 buildings and dozens (100's?) of computer labs. Most of the buildings were older and the labs were converted classrooms or other spaces. No new K-rated transformers were installed nor were any 200% neutrals. Power for the labs was just added to whatever was available.
I took numerous measurements with a Fluke 41 or 41B (can't remember now) harmonic analyzer. Not once did I ever find true RMS neutral current near any one of the phases or close to exceeding the conductor ampacity (pretty much all "full size" neutrals). I would routinely see high current distortion but voltage distortion was almost always under 3%. If it was higher than that it was not by much.
I do agree that, on paper, triplen harmonics will add but the distortion from PC's and other power supplies occurs at random angles and ends up having a cancelling effect anyway. In order to reach the 173% theoretical maximum neutral current you'd have to have condition just perfect for that with your loads and that just will never happen.
Again, anyone actually seen a transformer failure that you were absolutely certain was due to harmonic current and/or higher neutral current than phase current?
I never have and I've measured a bunch of locations. I'm wondering how much of this "problem" is scare tactic and how much is real. I know the trade magazine sure make a big deal out of it and have for years.
thanks,
bbaumer