Food Truck connection

Status
Not open for further replies.

Npstewart

Senior Member
Good afternoon everyone.

Im getting a lot of requests from clients asking to provide "a connection for a future food truck". Does anyone have a reccomendation as to what type of connection to provide? My thought was just to provide a junction box with an empty 1" conduit but would like to know what sort of load is associated with these things? I think they typically run on a generator which means they are likely 50A or 30A.

Any guidance would be appreciated.

FYI: I know these normally use a generator but im being asked to provide this because the food truck probably will always be there and they dont want it running on a generator near the building due to noise.

THANKS
 
I'd do the conduit/box and wait for the client to select a truck. IME, you' may see- 14-50 range plug, CS-6364/65 spider box plug, L14-30, 14-30(!), 30-amp 120v RV (TT-30), and there might even be L14-20s.

If have to wire it now, install either the CS or a 14-50R and see what they show up with.
 
It all depends on the truck clientele. They can have any type of connection that they want but that will depend on where they plug it in. Generally speaking it is a 30 amp receptacle but it could be or 50 depending on the needs of the truck
 
Last edited:
Many of the food trailers I deal with utilize a 50 amp 4 wire. Not to say they may need more or less.

Heck for a short while I had a guy that used to work for a power company and brought in a all electric fryer fish stand, said he wanted 200 amp and holy crap he needed it.
 
I always put in the CS-6364/65 and encourage food truck builders to use that.
If when they do events or move to a larger place like a fairground for a weekend then they will be all set.
1642558493762.png
 
I'd just install a 14-50 enclosed receptacle and let the food truck people deal with whatever adapters are needed. Food trucks always have the most messed up wiring. I see alot with two 5-15 inlets with the neutrals landed on the same busbar in a panel. Good luck plugging that into gfci.....
 