if you have a 400 amp service and the olny grounding method is a footer ground what size ground do you need.

250.66(B).

I see your an Inspector. Is this a trick question?:smile:

Welcome to the forum.
 

iwire

Moderator
Staff member
Location
Massachusetts
steven baker said:
if you have a 400 amp service and the olny grounding method is a footer ground what size ground do you need.

400 amp or 4000 amp service, the largest conductor size required to a concrete encased electrode will be a 4 AWG CU even if that is the only electrode available.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
steven baker said:
if you have a 400 amp service and the olny grounding method is a footer ground what size ground do you need.
It would depend on your how your ervice is installed. Generally it is as simple as T250.66 (#2 copper) but Note #2 can come into play

Edit: Sorry I was thinking water pipes.

Ground rods #6 Ufer #4
 
Last edited:

mistermudd

Senior Member
Location
Washington State
Footer ground. That is a new one for me. I see a lot of different terms from around the country on this forum. We are talking about an ufer or concrete encased electrode, right?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
mistermudd said:
Footer ground. That is a new one for me. I see a lot of different terms from around the country on this forum. We are talking about an ufer or concrete encased electrode, right?


Yes, a footer or footing ground is a CEE.
 