Gaffen99
Senior Member
- Location
- new jersey
Can anyone tell me why I am required to run a footing ground for an addition? I think I am missing something, if the service is grounded already, why the additional ground? Article #?
Is there steel in the footing? If the rebar is 1/2" or larger than the rebar is an electrode. The only exception is if you have to break up the concrete on an existing install.All electrodes are required, but I am installing the extra electrode in the form of a ground rod in the footing. It wouldn't be there if I don't put it there. IDK
The code requires that all electrodes present at the building be used--250.50. Now for an addition I think the ahj is going a bit far unless you are doing a service change.
if the service is already grounded,it's not required. have the inspector show you where he gets that it is. here's where it's req'd for new bldgs.2006 IRC E3508.1.1, E3508.1.2,E 3508.1.4, 2008 nec 250.52 (A)1, (A)(3), (A) (4), AND (A) (5), good luck:bye:
If I am not working on a service I think it could be argued that it is not in the job description.
If I am not working on a service I think it could be argued that it is not in the job description.
I get the bonding issue. That pretty much clears it up. Thanks. But, if the footing does not have rebar and is just a pour, I am not required to add an electrode, correct?
I get the bonding issue. That pretty much clears it up. Thanks. But, if the footing does not have rebar and is just a pour, I am not required to add an electrode, correct?
Now you tell us this.:rant:
I was told that there is no rebar, I have not been to the site yet. I was called late today and told that I need to do this and figured I would get some input on it.
Then it's simple, no rebar, no CEE required.
I agree. Since when does the NEC require us to bring the old service up to the new code?
So if you repipe your house with copper from PVC, you don't have to bond those pipes? I know the plumber didn't pull an electrical permit, but this just doesn't seem right. Adding a new ground electrode seems like a similar issue.
Not likely to happen and if it did then it should be bonded, IMO. Can they make you-- perhaps if it is part if the permitted work where an electrician is involved, There can be danger involved in non grounded piping but the lack of a CEE is not a safety issue.So if you repipe your house with copper from PVC, you don't have to bond those pipes? I know the plumber didn't pull an electrical permit, but this just doesn't seem right. Adding a new ground electrode seems like a similar issue.