HotConductor
Senior Member
- Location
- Philadelphia
Is this accurate when you have alot of fluctuating loads? I was FOP testing several points in a main distribution panel today and my readings were consistent between main bus(verticals) and bus stabs(horizontals) and between bus stabs and lugs on the load side of each breaker. But when I read between main bus and the load side of the breakers I was getting readings that kept changing.
FYI, I am troubleshooting an intermittent breaker tripping issue.
Also, I have one pb downstream from the mdp that has 10 amps on the egc going back to the mdp. I'm thinking the best way to find the source of this is to start shutting off breakers one at a time until the current drops off?
FYI, I am troubleshooting an intermittent breaker tripping issue.
Also, I have one pb downstream from the mdp that has 10 amps on the egc going back to the mdp. I'm thinking the best way to find the source of this is to start shutting off breakers one at a time until the current drops off?