goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I went on a service call yesterday after a HO called said that on Xmas day they heard a pop in the kitchen and then started to smell things burning in several rooms. They began unplugging everything they could. Unfortunately.....they were too late. Some 15 or 20 years ago the rocket scientist who wired their kitchen decided to run a 12/3 RX to a kitchen counter JB and back-stab the feed neutral into the receptacle (BTW, there were no GFI's in the kitchen). Wrapped around the screws were the neutrals feeding each of the two MWBC's. Aside from the receptacle and wires burnt at that location the following appliances were among the victims : refrigerator, microwave, range-oven, computer, monitor, modem, (CATV box, television, stereo, VCR in the next room). He mentioned that his insurance was $5K deductible. I think he's exceeded that. In addition to those problems I checked the breaker panel. Each neutral was landed on the ground bar along with its respective EGC under the same screw. Several (including the MWBC in question) were loose. I'm surprised this house didn't burn down.