Foreign pipe running through electric room

Status
Not open for further replies.

mshields

Senior Member
Location
Boston, MA
At a preliminary punch out of a job, I discovered that the plumbing contractor had run the main sprinkler pipe through my main electric room. The proposed solution was to soffit around the pipe with 2 hour rated gype board.

I'm not so sure I'm comfortable with this. Circumstances are such however, that if it's within code, I'm going to have to live with it. Would very much appreciate your input.

Thanks,

Mike
 
mshields said:
At a preliminary punch out of a job, I discovered that the plumbing contractor had run the main sprinkler pipe through my main electric room. The proposed solution was to soffit around the pipe with 2 hour rated gype board.

I'm not so sure I'm comfortable with this. Circumstances are such however, that if it's within code, I'm going to have to live with it. Would very much appreciate your input.

Thanks,

Mike

What code section did he violate?

Jim T
 
mshields said:
At a preliminary punch out of a job, I discovered that the plumbing contractor had run the main sprinkler pipe through my main electric room. The proposed solution was to soffit around the pipe with 2 hour rated gype board.

I'm not so sure I'm comfortable with this. Circumstances are such however, that if it's within code, I'm going to have to live with it. Would very much appreciate your input.

Thanks,

Mike


Like it or not it may be ok
110.26 (F)

(b) Foreign Systems. The area above the dedicated
space required by 110.26(F)(1)(a) shall be permitted to contain
foreign systems, provided protection is installed to
avoid damage to the electrical equipment from condensation,
leaks, or breaks in such foreign systems.
(c) Sprinkler Protection. Sprinkler protection shall be
permitted for the dedicated space where the piping complies
with this section.
 