fork lift battery charger

Status
Not open for further replies.

Big Jerm

Member
Location
Columbia, SC USA
I went to a call at a building that is being served by a delta 3 phase 4 wire 120v/240v/ 208v high leg. from phase to phase is 240v from C phase to grnd it is 208v then a,b to grnd is 120v.
The call was to hook up a fork lift battery charger (3 phase 208/240/480/600 VAC) that is preset for 480 VAC Star connection. how can I make this work, I have a 3pole 240v breaker and that is the voltage I will use, simply by using the 240 connection but will it work the charger correctly without re tapping the X-fmr for delta connection?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Sounds like you need to change the internal charger taps to match your 240 v system
 
Status
Not open for further replies.
Top