Looking for clarification on a project I didn’t get to do. Is the other contractor to code or was I over building.
Scenario- Feed two battery chargers for fork lifts from a 100amp bucket, voltage 480v each charger draws 39.4 amps from nameplate.
I recommend 90amp fuses with 3awg to 6x6 box between disconnects to split off to both disconnects with 3awg, fused disconnects with 40 amp fuses.
What is being installed is 80amp fuses with 8awg to both disconnects non fused with both 8awg landed on bottom side of bucket.
Go easy on me my first post
Scenario- Feed two battery chargers for fork lifts from a 100amp bucket, voltage 480v each charger draws 39.4 amps from nameplate.