If a Form 7 conduit body is installed in this application can you make a splice in the conduit body.
Class 1, Division 2
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
If a Form 7 conduit body is installed in this application can you make a splice in the conduit body.
Class 1, Division 2
I wouldn’t see why not. Just watch for the cu in marking inside. They don’t have a whole lot of room to stay complaint if you are splitting off several different ways. (Plenty of ways around that though if you get creative).

From what I recall wirenuts arnt and shouldn’t be considered arcing/sparking devices.

Sorry I have no code ref to share being lazy and shooting from my mind.

Someone here directly will have the info to back it up.
 
Last edited:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
In Class I, Division 2, apart from sealing requirements most metallic raceway wiring methods are acceptable, “as-is”. See Section 501.10(B)(1) and its cross reference to Section 501.10(A)(1)
 