tonytonon said:I googled it since my mind is gone..
KW = KV X Amps X PF X 1.73 so assuming 0.8 power factor:
45KW = 0.208KV X Amps X 0.8 X 1.73
Amps = 45 / .208 X .8 x 1.73
Amps = 45 / .2879
Amps = 156.3A
? someone pls check this
I agree, just don't convert HP straight to KW.Jraef said:This is close enough if it is a motor or other inductive load, also a safe bet if it is a mixed load.
I don't follow you.jim dungar said:I agree, just don't convert HP straight to KW.
Besoeker said:I don't follow you.
In what circumstances would the conversion be the wrong thing to do?
I see what you are getting at.jim dungar said:When many people try to determine the input KW of a motor which is rated in output HP, by simply converting HP to KW, they forget to account for the efficiency of the motor.