Basic formulas for resistance heating:
P=I*E
E=I*R

Working the math the hard way
R=E^2/P -> Rheater=Eold^2/Wold -> Rheater=240^2/10,000 ->Rheater=5.76Ohms

Pnew=Enew^2/Rheater -> Pnew=208^2/5.76 -> Pnew=7,511W -> 7.511KW

Working the math the easy way
Pnew=Pold*((Enew/Eold)^2) -> 10KW*(208/240)^2 -> Pnew=7.52KW
 

luke warmwater

Senior Member
Re: formula

Even easier(this is single phase, I take it?):
R=E(E/P)
R=240(240/10000)
R=5.76ohms
I=E/R
I=208/5.76
I=36.11amps
36.11x208=7511.11watts

Easier yet:
(208/240)squared=.7511
.7511xwatts
.7511x10000= 7511watts= 7.51Kw
 

brad troxel

Member
Location
Minnesota
Re: formula

Even easier yet,
Watts, is Watts, is Watts,
you will always have 10kw, your currrent will change with your voltage. You size your wire by the wattage of the equipment, your watts on the water heater won't change unless you buy a different wattage element. Look at the element at the hardware stores, anywhere from 2500w to 10kw.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: formula

Brad,
Look at the math in the previous posts. Ohm's law does apply. The heating element has a fixed resistance and both the current and watts will change when you change the voltage.
Don
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: formula

Brad, as Don said look at the earlier posts.

We recently wired a 180kw 240v 3ph steam generator with 208v 3ph. This did allow us to change wire size, and at this size wire, there is a difference if bidding a job.