I am installing some of these cans. The Jbox is marked max 4 #12's. The actual inside measurements of the box are 1?"?4?"?3?".

1?"?4?"?3?"=23cubes.

23cu/in?2.25=10 #12's.

How did they come up with a max of 4?
 

celtic

Senior Member
Location
NJ
I am installing some of these cans. The Jbox is marked max 4 #12's. The actual inside measurements of the box are 1?"?4?"?3?".

1?"?4?"?3?"=23cubes.

23cu/in?2.25=10 #12's.

How did they come up with a max of 4?

I think you may have misread the instructions/fill:

? UL Listed for through branch
circuit wiring (maximum 8
No.12 ga., 90?C conductors).
http://www.cooperlighting.com/specfiles/pdf/Halo/H1499ICspecsheet.pdf


I think I have some of those cans laying around...lemme go check

PLEASE STAND BY......
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
halo.jpg


Is this a typo? Connectors suitable for 90?C?
 

480sparky

Senior Member
Location
Iowegia
So I can figure conductor fill as per 314.16?

I would think the labeling would over-ride the NEC since it's more restrictive in this case.

I don't think you can multiply the dimension of a known jbox and use it to calculate box fill
Take a standard 4x4x1?. Works out to 24in?. But T314.16(A) states the volume as 21in?.
 
Last edited:

celtic

Senior Member
Location
NJ
The spec on my cans are a bit different:

1108081453.jpg


1108081451.jpg


Close up:
1108081452.jpg


I don't know if you can see it...says (6) #14s :-?


Under that sticker, it's back to 8 #12s [again, crappy cell shot, sorry if you can't read it]
1108081452a.jpg


The instructions that come with the can make no mention of wire fill
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I still think you are limited to 4 12/2 cables or the equivalent-- it should be the same as 314.16 or purtie close.

Yup, and I agree with your earlier post, poorly written.

I would think the labeling would over-ride the NEC since it's more restrictive in this case.

110.3(B)?:smile:

I don't think you can multiply the dimension of a known jbox and use it to calculate box fill
Take a standard 4x4x1?. Works out to 24in?. But T314.16(A) states the volume as 21in?.
Those are outside dimensions.
 

celtic

Senior Member
Location
NJ
I would think the labeling would over-ride the NEC since it's more restrictive in this case.

I agree....BUT...if one is suing #12s and the label says "Max (6) #14s" then what?

6 #14s = 6 x 2.00 = 12cu. in.
12cu. in/2.25 = 5 #12s ?

That JB is HUGE ...so much for running a 3 wire NM to save money or for switching purposes.

2 #14/3 = 7:mad:
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I don't think you can multiply the dimension of a known jbox and use it to calculate box fill
Take a standard 4x4x1?. Works out to 24in?. But T314.16(A) states the volume as 21in?.
I bet you could if you used the actual interior dimensions, and not the box's nominal size.
 