four-or-more fastened in place appliances

Status
Not open for further replies.

TimWA

Member
220.53 allows a 75% demand factor for four or more of certain types of appliances fastened in place.

Is this applicable to a multi-unit total or per unit only?

Eg. If I have only two such appliances per unit in 20 units, will I still apply 75% because I have a multi-unit total of 40 appliances?

thanks,
-Tim.
 

bphgravity

Senior Member
Location
Florida
Re: four-or-more fastened in place appliances

Yes, your example is correct. Section 220.53 lists multifamily dwellings as includied in the demand allowance. The individual feeders to each unit can only include the appliances served by that feeder, but the service can have the demand applied since it will serve all the appliance loads.
 