FP ATS tap into paralleling gear bus

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
All items described below are 480V/3PH.

We have (2) existing generators to feed a paralleling gear.

We add a new fire pump ATS that serves the building fire pump, the ATS utility feeder was tapped into building utility xfmr secondary side.

We plan to connect ATS emergency feeder to above paralleling gear, however the paralleling gear has no space left to add a new breaker in distribution sections to serve fire pump.

Can we tap into paralleling gear bus to feed the fire pump ATS (assuming we will comply with 10' tap rule)? Because this is fire pump, I read through 695 but not sure if I missed anything that prevents this connection.
 