That is the maximum ambient temperature for the breaker. You do not use this temperature in any conductor ampacity calculation.We have an existing FPE 225A circuit breaker with a sticker that states the breaker is rated at 40d C CU-AL Conn. How do I calculate the ampacity of the load conductors at 40d C?
There is really no reason to even include the 40 degree C marking on the CB. It just causes unnecessary confusion.I assumed that but the 40d C threw me off. I thought that referred to the temp of the terminals.
I think it may be a 'standards' requirement. I can't think of ever seeing a molded case breaker without it.There is really no reason to even include the 40 degree C marking on the CB. It just causes unnecessary confusion.
You're probably right, something that's been there for decades but most electricians have no idea what it means.I think it may be a 'standards' requirement. I can't think of ever seeing a molded case breaker without it.
That's actually the basis for the UL489 listing of molded case circuit breakers. The only time it is different is if you NEED a higher temperature rating, for which you pay through the nose. I once had to buy some breakers rated for 60C operation (in a boiler room of a ship), they were 5x the cost of a standard breaker. Extreme cold requires special breakers too by the way.You will see this max 40 degree rating on almost every molded case breaker, you can find.
Yes, but I've always wondered why it needs to be shown on a standard breaker.That's actually the basis for the UL489 listing of molded case circuit breakers. The only time it is different is if you NEED a higher temperature rating, for which you pay through the nose. I once had to buy some breakers rated for 60C operation (in a boiler room of a ship), they were 5x the cost of a standard breaker. Extreme cold requires special breakers too by the way.
The size and shape of the internal mechanism is different at different temperatures. Parts can go out of tolerance if it gets hot. If it isn't tested at higher temperatures, there's no guarantee it will work.Yes, but I've always wondered why it needs to be shown on a standard breaker.
to confuse peopleYes, but I've always wondered why it needs to be shown on a standard breaker.