Quote:
Originally Posted by don_resqcapt19
Be careful with thinking that a lower available fault current always means a lower incident energy. I just got an arc flash hazard "slip stick" from Littelfuse. It says it is for 600 volts and less, but I expect that is applies mostly to 480 volt systems as the arc tends to self extinguish at each zero crossing for lower voltage systems.
Don, aren't you reaching that same zero crossing regardless of voltage? Isn't it going to depend on the resistance and the distance arc has to travel? In my mind the higher the voltage the more space you need to prevent the start of an arc as opposed to lower voltage. When you use a carbon arc type machine to cut metal, I believe what you say is true, the arc will self extinguish a the zero crossing. However, that 1/60 of a second is not real noticeable regardless of the voltage.
Does this mean lower voltage systems don't have an issue? Or at least can we say a 120/240V service needs to be a certain size before it is?
IMO a 30A service has the same issues as a 600A service if they are both fed off same xfmr.
Quote:
They show that for a 101 to 200 amp RK1 or Class L fuse, you would need protection Level 0 for fault currents above 4kA, Level 2 for a fault current of 2kA and Level X (incident energy exceeds 40 cal/cm^2 and energized work is not permitted) for a fault current of 1kA. For breakers in the same size range they show Level 1 for fault currents of 16 to 60kA, Level 0 for 4 to 14kA and Level X for 2kA and under.
Don
So how can you ever be safe? How can you guarantee you have at least 4kA or whatever of fault current? I can see how you can find a maximum fault current, limited by the transformer, wire, etc, but not how you can find a minimum.