(G) Conductors for Small Motors.
Conductors for small motors shall not be smaller than 14 AWG unless otherwise permitted in 430.22(G)(1) or (G)(2).
(1) 18 AWG Copper.
Where installed in a cabinet or enclosure, 18 AWG individual copper conductors, copper conductors that are part of a jacketed multiconductor cable assembly, or copper conductors in a flexible cord shall be permitted, under either of the following sets of conditions:
The circuit supplies a motor with a full-load current rating, as determined by 430.6(A)(1), of greater than 3.5 amperes, and less than or equal to 5 amperes, and all the following conditions are met:
The circuit is protected in accordance with 430.52.
The circuit is provided with maximum Class 10 or Class 10A overload protection in accordance with 430.32.
Overcurrent protection is provided in accordance with 240.4(D)(1)(2).
The circuit supplies a motor with a full-load current rating, as determined by 430.6(A)(1), of 3.5 amperes or less, and all the following conditions are met:
The circuit is protected in accordance with 430.52.
The circuit is provided with maximum Class 20 overload protection in accordance with 430.32.
Overcurrent protection is provided in accordance with 240.4(D)(1)(2).
(2) 16 AWG Copper.
Where installed in a cabinet or enclosure, 16 AWG individual copper conductors, copper conductors that are part of a jacketed multiconductor cable assembly, or copper conductors in a flexible cord shall be permitted under either of the following sets of conditions:
The circuit supplies a motor with a full-load current rating, as determined by 430.6(A)(1), of greater than 5.5 amperes, and less than or equal to 8 amperes, and all the following conditions are met:
The circuit is protected in accordance with 430.52.
The circuit is provided with maximum Class 10 or Class 10A overload protection in accordance with 430.32.
Overcurrent protection is provided in accordance with 240.4(D)(2)(2).
The circuit supplies a motor with a full-load current rating, as determined by 430.6(A)(1),^ of 5.5 amperes or less, and all the following conditions are met:
The circuit is protected in accordance with 430.52.
The circuit is provided with maximum Class 20 overload protection in accordance with 430.32.
Overcurrent protection is provided in accordance with 240.4(D)(2)(2).